I wonder how the Multi RS performs in combination with a 5kW general purpose generator.
When I connect our generator to our Multiplus 2 (48/5000/70) I am only able to charge at a limited power (+/-50%) due to the a hunting AVR on the generator, when I switch off “Weak AC”.
The Multi RS has different hardware (HF) and I want to know if that makes a difference in this regard.
I don’t have Multi RS yet, but it could be a sollution for us, as it is cheaper then replacing the generator.
At the moment I have a dedicated MP2 for charging, because I don’t want the generator to power our complete system.
It would be nice to be able get more from our generator without overloading it, or having to buy a new havier one that also might struggle.
Currently I am using a 5kW MP2 in combination with our generator, and there is a limit around 2.5kw. Weak AC is on, UPS off, even when I raise the allowed input current it won’t go above 2.5kW, it just keeps it around that power. I experimented with the settings, and at some point it didn’t hunt with Weak AC OFF, and was able to draw more power, but it was not reliable everytime. If I could only get 1-1.5kW more I would already be very happy.
We have the generator already for a few years, and bought it when we didn’t have a off-grid system yet. It does run fine with other loads, I could check it again running with high loads to be sure. We live in central Portugal at about 250m height. We bought it at a local shop and they made sure back then it was running fine. I suspect the AVR has difficulties with the way the MP2 loads the generator when charging. When the Multi RS (solar) does not have this ‘problem’ it is a viable solution especially when it also adds 2 mppt’s to the system. I will then add the current MP2 in parallel to the other 2 I have already running.
It is locally used in the workshop and as charger. The other 2 provide power for the rest of the property and over time it is good to have more power available for expansion.