Generator working better on a Multi RS (solar) compared to MP 2?

I wonder how the Multi RS performs in combination with a 5kW general purpose generator.
When I connect our generator to our Multiplus 2 (48/5000/70) I am only able to charge at a limited power (+/-50%) due to the a hunting AVR on the generator, when I switch off “Weak AC”.
The Multi RS has different hardware (HF) and I want to know if that makes a difference in this regard.

I don’t have Multi RS yet, but it could be a sollution for us, as it is cheaper then replacing the generator.

At the moment I have a dedicated MP2 for charging, because I don’t want the generator to power our complete system.

It would be nice to be able get more from our generator without overloading it, or having to buy a new havier one that also might struggle.

Thanks in advance for any advise.

The RS doesn’t load the generator the same way the MP2’s do as their topologies are very different. (As you know)

I hope someone has any positive experiance with the Multi RS and a generator compared to the MP 2.

That could save me finding it out myself and I may choose a different sollution.

Mogelijk dat Harold Halewijn van het ‘Slimmehuis’ (forum lid en Victron Installer) hierop een antwoord heeft, niet geschoten is altijd mis.

I haven’t had issues with the RS and generators.

Did you use a 5Kw general purpose generator, and upto what power are you able to load it?

Because we are at a higher altitude at about 3kw.

General calculation kVAx 0.8 x 0.8. and maybe if it is an older well used unit, slightly less.

Currently I am using a 5kW MP2 in combination with our generator, and there is a limit around 2.5kw. Weak AC is on, UPS off, even when I raise the allowed input current it won’t go above 2.5kW, it just keeps it around that power. I experimented with the settings, and at some point it didn’t hunt with Weak AC OFF, and was able to draw more power, but it was not reliable everytime. If I could only get 1-1.5kW more I would already be very happy. :slight_smile:

So at 2.5 you are close. Is the genset tuned right?

What’s your altitude?

We have the generator already for a few years, and bought it when we didn’t have a off-grid system yet. It does run fine with other loads, I could check it again running with high loads to be sure. We live in central Portugal at about 250m height. We bought it at a local shop and they made sure back then it was running fine. I suspect the AVR has difficulties with the way the MP2 loads the generator when charging. When the Multi RS (solar) does not have this ‘problem’ it is a viable solution especially when it also adds 2 mppt’s to the system. I will then add the current MP2 in parallel to the other 2 I have already running.

So this one was just used as a charger? Was it in charger only mode?

It is locally used in the workshop and as charger. The other 2 provide power for the rest of the property and over time it is good to have more power available for expansion.