Generator Running during cool down period but does not shed loads

I will be changing locations tomorrow, staying in a RV park for 4 days and then off to the desert.

I updated the software to v3.54. When in the desert, I run the generator daily for battery recharge. I will see if the warm up/cool down function will work in v3.54.

I still would like to know how the generator ‘unloading’ for warm up/ cool down is accomplished. Is there a write up somewhere that explains how the software accomplishes this function? I know that using Assistants can tell the Multiplus IIIs to ignore the AC input even though it is connected. Would that function be the one that the software is supposed to control during warm up/cool down time?

I am running the two Multiplus IIs in a parallel configuration. Could the software be telling one of the Multiplus IIs to ignore AC input but not the other one?

When I first tried the Warm up/Cool Down features, I remember being told that the Cerbo needed two digital inputs to tell it that the generator was running. I cannot find that post and suspect that it was on the old post system. Does it make any sense that the Cerbo would require two digital signals to tell it that the generator is running? I only have one signal but I can parallel it into two digital inputs. The Cerbo already reports correctly when the generator is running, but if telling twice is needed, I can do that.

Any thoughts are appreciated.