Generator autostart - inventer overload delay not working?

Does the delay in cerboGX mk2 work for generator autostart - inverter overload? Even though I have it set to 20s, the relay in cerbo clicks as soon as the overload on the multiplus II starts flashing.

tested on 3.60 - 66.

In AC load settings, for example 4000W on the highest phases, the timer works. But as soon as enable in inverter overload, the generator switches on as soon as the overload LED starts flashing.

Bug?

I had more time today so I tested more.

cerbo mk2, 3xmultiplus II 5000/48, 3f configuration,
Beta 3.60~69 - generator autostart condition

AC Load condition work OK. Short time exceeding of set values ​​does nothing. After time exceeding, generator will start.

inverter overload - even a short overload will still force the generator to start after the set time has elapsed, even if the inverter is no longer overloaded.