Hi,
I have the following setup:
- Victron MultiPlus-II 48/10000/140-100/100
- Cerbo GX (firmware v3.73)
- 2x Fronius Primo (4.6kW and 5.0kW) on AC-output
- 4x Voltsmile V10 batteries in parallel (20kWh / 400Ah)
- Carlo Gavazzi grid meter between Linky and MultiPlus
- Single phase, French rural grid (Enedis), max feed-in contract 12kW
Current ESS settings:
- Grid metering: External meter
- Grid setpoint: 100W
- Max feed-in power: 1300W (limited by voltage rise on weak grid)
- Max charge voltage: 55.2V
- Min SOC: 25%
- ESS mode: Optimized with phase compensation
- AC-coupled PV feed-in excess: enabled
- Fronius: Cos φ = 1.000, Dynamic power reduction: No Limit
Problem:
On sunny days with variable cloud cover, the Fronius inverters shut down every few minutes. This causes the MultiPlus to switch to Inverting mode, the battery discharges at -70A to compensate, and after 60-90 seconds the Fronius restarts — then the cycle repeats.
I have identified two separate causes from Home Assistant history graphs:
-
Grid frequency instability — the Enedis grid frequency regularly drops to 49.1Hz or rises to 50.6Hz. This is a known issue with weak rural French grids.
-
Overproduction when battery is full — when battery reaches ~90-95% SOC and PV production fluctuates rapidly due to clouds, the MultiPlus applies frequency shifting to reduce Fronius output. The frequency shift causes the Fronius anti-islanding protection to trigger and shut down.
What I have already tried and fixed:
- Fixed grid metering from “Inverter/Charger” to “External meter” — this solved the main oscillation issue
- Lowered max charge voltage from 57.6V to 55.2V to maintain battery buffer
- Disabled Fronius Smart Meter (was incorrectly placed between Fronius and MultiPlus, not at grid connection point)
- Set Fronius Cos φ from -0.900 to +1.000
- Set grid setpoint to 100W
- Weak AC input: disabled
Remaining problem:
On days with rapidly changing cloud cover and battery above 85% SOC, the system becomes unstable with Fronius shutdowns every few minutes. Maximum feed-in is limited to 1300W due to voltage rise on the weak rural grid (voltage exceeds 253V above 1300W feed-in).
Questions:
- Is there a way to slow down the frequency shift ramp rate in ESS to give the Fronius more time to respond gracefully instead of triggering anti-islanding?
- Are there any ESS Assistant settings in VEConfigure that could improve stability for AC-coupled PV on AC-output with a weak grid?
Any help appreciated.
Thanks