I have an offgrid Victron Multiplus 5Kw, fronis inverter 5Kw (in MG50 mode), MPPT RS 450/200, 30kwh 48v lithium battteries with pylontech BMS
The problem is that when the battery is fully charged and a big load (toaster) disconnects suddenly the voltage surges up to 60v momentarily throwing a battery overvoltage error on the cerbo.
I decreased the fequency values in ESS slightly, but it still uses the AC coupling before the DC coupling.
Should I just keep decreasing the fequency values in ESS until DC coupling takes priority or is there a better way to make big loads draw from the DC side when at 100% charge?
As far as setting up the fronius I used the following instructions, there wasnt much to do except update to latest firmware and switch it to MG50 mode.
1.3 Setting up the Fronius with Setup MG50/MG60
When not pre-ordered with a MicroGrid setup, follow these steps:
Make sure that the Fronius PV inverter is updated to at least the firmware version mentioned above. See Inverter list above.
After making the inverter operational according to the manual, select the language and after this the country specific setup.
Here choose MG50 or MG60 depending on the system frequency.
I’m curius why the DNO settings requirements would be listed in the AC-coupled PV with Fronius PV Inverters [Victron Energy] document as something that needs to be done for on-grid ESS design installation manual but not mentioned in off-grid insructions. I will give that a go - Thanks.
Yes Fronius is using wifi and is seen correctly in GX
I’m still getting the error messages that happens when the batteries are 100% and a high power device is instantly switched off like a toaster popping up.
In this instance all the power is coming directly from either the RS or the fronius and they cant respond to the sudden reduction of load quick enough and throws an error.
Which guide are you referring to? I’m using PV intereter assistant. https://www.victronenergy.com/live/ac_coupling:fronius
I looked through this guide and I cant see anything about programing voltage to 51v and 52v.
Pease let me know.