Hello,
I have an interesting scenario/s with my workshop solar setup.
I have set up a 48/5000 Multiplus II, along with a Pylontech battery, Cerbo-GX II, Smartsolar MPPT and a Fronius Primo 5.0-1 inverter connected to the AC output and communicating through a direct LAN to the Cerbo-GX II.
Now, everything for all intensive purposes works well and communicates well, except for the Fronius Primo. Although it reliably feeds its data back to the Cerbo-GX and displays everything well, it does not appear to make any attempt to throttle power output under the victron frequency control. The Victron adjuasts the frequency up until the Fronius cuts out on “High frequency cut out”. And to add to the frustration, I bought the Fronius second hand, still under warranty and in very good order. That being said, the original installer, who has now shut up shop, appears to have the admin and owner rights, so I cannot transfer the system from the person I bought it off. His settings page on solarweb.com does not allow for change of owner. I have contacted Fronius help team regarding this and waiting for a reply.
Here are a few point forms to try to lay it out better.
-
All units, including the Fronius, have the latest firmware installed and double checked.
-
Multiplus II is new and shifting frequency smoothly.
-
Fronius is almost new, but second hand and “locked” to a degree. (in progress with tech help).
-
Fronius is not responding to frequency and just puts in full power available from panels until tripping out on high frequency signal from Multiplus.
-
Fronius has FILmin at 47,00Hz. I set the start on Victron Assistant at 50,20Hz as recommended.
-
Fronius has FILmax at 52,00Hz (as opposed to the usual documented 52.80Hz). I set the reduced to minimum at 51,90Hz and the disconnect at 52,20Hz, due to the differences.
-
Fronius does trip once frequency goes above 52,00Hz.
-
Fronius does not appear to respond to any frequency between 49,90Hz and 51,90Hz. The unit just gives full available solar power until tripped.
-
Testing has been carried out under minimal load, medium load and heavy load (allowing the Multiplus to still be in a “charging” state). The results are always the same.
-
I have been through everything that I can access on the Fronius screen and cannot appear to change the situation.
*I have tried cold boots on all systems, with no change.
I hope someone here may be able to shed some light on the current situation.