Grid failure leads to erratic ESS system

A short update:

  1. The battery voltage has been down adjusted to absorption 54.5V and float 54V. Many thanks for Cluj Napoca, Victron dealer for great support.
  2. The Fronius frequency shift values adjusted in ESS Assistant to: 51.00 / 53.10 / 53.20, after reading this post

Up to now it has tested OK during grid removal and restore, though with a 50% SoC battery.
Will do more test after reaching 100% SoC and still PV production.