Your plan is generally on the right track, but let’s clarify your conductor requirements and bonding concerns for safely wiring the Multiplus II in your RV.
Neutral and Earth Conductors
You cannot omit any conductors, even if the neutral and earth are bonded at the service panel. Here’s why:
Neutral Conductors:
The neutral wire is a current-carrying conductor and forms part of the circuit for return current from connected loads.
A dedicated neutral conductor must run both to and from the Multiplus, as the inverter will switch or interrupt the circuit during certain operations. This ensures safety and proper operation.
Earth (Ground) Conductors:
The ground wire provides a safety path for fault currents.
While the ground and neutral are bonded at the service panel, they serve distinct purposes in the system. You must run a separate earth wire to the Multiplus and back to maintain code compliance and safety.
Conductor Count
Given that you’re wiring a 30A system with a feed and return setup:
Feed: Hot (L), Neutral (N), Ground (G) to the Multiplus.
Return: Hot (L), Neutral (N), Ground (G) back to the service panel.
This results in a total of 6 conductors (3 for the feed and 3 for the return).
Conduit Fill
You’re correct that a 3/4" flexible non-metallic conduit can accommodate six THHN/THWN conductors without exceeding fill limits for 30A. For instance, using #10 AWG wires (appropriate for 30A circuits) is within acceptable limits.
Code Compliance and Safety
Ensure all wiring adheres to the National Electrical Code (NEC) or your local regulations, especially for RVs.
Use the proper breaker size (30A) to protect the conductors.
Verify that the Multiplus inverter’s neutral-ground bonding relay aligns with your wiring plan. The inverter automatically bonds neutral and ground internally when operating in inverter mode and will disconnect when needed for externally bonded input. Check the manual to avoid redundant bonding that can create safety hazards.
Summary
Yes, you need to run all six conductors:
Feed: L, N, G
Return: L, N, G
This ensures proper operation of the Multiplus, maintains compliance with safety codes, and avoids potential hazards. Your plan to use 3/4" conduit is solid and should comfortably accommodate the wiring.