Late in the afternoon when I don’t have any excess solar, the EVCS keeps trying to charge my car. It will repeatedly start and stop charging within a few minutes or even seconds. This is all occurring around 91% SOC. How can I keep it from doing this quick on and off charging?
Can you share more about your equipment and your vehicle’s charging needs?
eg a quick look at your settings suggest that when the batteries exceed 90% SoC it starts charging the car as expected.
But then it draws power - likely drawing down the batteries.
So how much battery capacity do you have? How much is the car drawing? How much non-PV power is available?
e.g. EVCS input of 28A * 230V = 6.5kW, which assuming battery side is 48VDC 100Ah and 100% efficiency is 134A, with 80% DoD, that would last about 35 minutes at best.
I have two Multiplus II’s providing 120V and 240V, Cerbo GX, four 100AH SOK 48V batteries.
The 28A is not an EVCS setting. That is the AC In limit set in the Multiplus II’s.
The EVCS does start charging at 90% as expected. That is when solar power input to the battery typically slows down. Most days that occurs around 2pm to 3pm. At that time there is plenty of excess solar to begin charging the car up to a max of 13A. The problem starts late in the afternoon, when there is no excess solar. The EVCS will stop charging the car for a period of maybe 10 minutes and then cycle on and off for periods lasting seconds to a few minutes.
Since I have “Allow battery/grid power for auto mode” disabled, I would expect Auto Mode to sense or calculate via algorithm that there is insufficient excess solar and stop charging for a substantial period (say 30 min) before checking in again to see if there is excess solar. Rapid cycling of charging seems like a failure of the Automode algorithm.
If you temporarily enable “Allow low excess solar power for auto mode” (Which will draw power from the grid to make up the difference from the 1.4kW needed vs what solar is giving you) how does it behave? Just trying to eliminate the communication between EVCS and Ioniq as a factor.
Are all the mechanical connections good and solid? Nothing loose, no problems with the connector seating?
To answer the question from the first post, that’s the only way the EVCS will know if there is excess power, by probing.
If the PV power is not enough it will stop. If the SOC is lower than defined, it will stop trying. Or if the system is already consuming from the battery.
Especially for off-grid installations or for systems where it is not allowed to feed back into the grid, there is no other way because in these cases, the PV power is reduced.
You can increase the start SOC to something higher, like 95%, play with the settings, and see what is best for you. There are no universal settings that are suited for all the systems.
I have also experienced this issue with auto mode not working as I think it should. It seems to happen anytime that the battery is above start SoC but solar is not nearly enough to supply the minimum charge rate, I.e. 300W coming in. I have seen this on sites in early morning and late afternoon.
Settings, off grid solar system, start SoC = 80, stop SoC = 30, “Allow battery/grid power for auto mode” = enabled, “Allow low excess solar power for auto mode“ = disabled, “Battery/grid power timeout (min)” = 15mins, 6kWp, EVCS firmware version 2.08, GX firmware version 3.75
What happens
if battery is above “Start charging at backup battery SoC” value
solar power being made is low I.e. 300W
EVCS starts charging
the “Stop charging in” timer immediately starts counting down
when the “Stop charging in” timer reaches zero then the EVCS stops charging
the EVCS immediately then shows a “Start charging in” timer of 1min 30s and counts down
once timer is at zero the EVCS then starts charging again and the Stop charging in” timer immediately starts counting down
this cycles just keeping repeating until the battery is below start SoC and then one last “Stop charging in” timer counts down and then the EVCS stays off until battery is above start SoC again
What should happen
if the “Allow low excess solar power for auto mode“ setting is disabled the EVCS should not start when there is only 300W of solar coming in at 07:00 in morning!
it is as if it ignores that setting
it is clear the EVCS knows there is not enough solar immediately after it turns on as it then starts count down to turn off
why does it wait 1min 30s and then start again when the solar coming in is still low?
yes it needs to do the probing behaviour to find out how much excess solar is available but it should not be doing this when solar generation is so low?
Summary of my issue with the auto mode
It is starting when there it too little solar and repeatedly cycling on, countdown timer of grid/battery use max time then off, then on again etc. It should not turn on until there is enough excess solar to run 1.3kW minimum charge rate. And if it does turn on before this to try to probe if there is more excess solar it should realise after one or two cycles that there is not enough solar generation and not just repeatedly turn on and then off using majority battery power
Just observed the EV charger coming on with 90W of solar present as panels are in shade at the end of the day and it just doing the cycle described above, start charging, immediately start battery timeout count down, then turn off and show “Waiting for sun” status as it should but then it turns on again and starting charging and then immediately starts counting down the battery timer.
This is clearly broken and not working as it should, the charger should be in the “waiting for sun” state until battery goes below EVCS start charging SoC when it will then go to “Low SoC state.