Is an ESS with ONE MultiPlus RS (Solar) possible on a 3-phase grid?

I’m currently reading through the Multi RS manual, and I’m wondering whether you can build an ESS system with ONE MultiPlus RS (Solar) on a three-phase grid, or whether you need 3 MultiPlus RS (Solar) units, as shown in the manual?

The Multi RS is quite different from the other MultiPlus models with a transformer, hence the question.

The forum search seems to show that there are users with a single MultiPlus RS (Solar) on a three-phase grid…

Hi Dirk, I assume it would work fine, but that it’s not allowed because you’d create a phase imbalance.

The grid code generally limits the phase imbalance to the permissible range, which here would be 4.6 kW.

I’m no expert, mind, and even less so when it comes to Germany :slight_smile: But your imbalance will be greater than that 4,600 W, because you’re using power on the other phases at the same time.