I am considering to purchase an EasySolar II GX for building a domestic ESS system. Have studied the manual - looks really nice. My question concerns the built-in battery monitor: is that the one inside the Multiplus ? If so, then it would not measure charge current from the MPPT.
I would expect that the battery monitor provides an overall measurement of all charge and discharge currents flowing into/out the battery, but cannot find it with so many words in the manual. Can someone confirm that this is indeed correct ?
The easysolar is a standard Multiplus with a GX board and Mppt in one housing.
The MP GX does not offer all the connections of a Cerbo GX. In particular, it only has one CAN connection for the a managed battery and NO additional CAN port for a CAN bus solar charge controller, only one USB port and one VE.direct interface.
The MultiPlus implements a “software battery-monitor”. Also known as “built-in battery monitor“.
The Venus OS software running on the GX card includes the option to send “corrections” to compensate for MPPT current charging the battery.
The setting is called “Use solar charger current to improve VE.Bus SoC“
But, as you probably realize, the accuracy is not great.
For the best accuracy, install an external battery monitor (BMV-712 or SmartShunt) and connect it via VE.Direct to the GX card.
Most managed Lithium batteries also measure the SoC and if it’s connected to the CAN port of the GX card, then the system will use the SoC reported by the BMS.
For cheap Chinese batteries with cheap BMS, the SoC accuracy is terrible and I strongly recommend a Victron SmartShunt.
Thank you for the clear answer !
I think it would be a great addition to the “all-in-one” easysolar if Victron would include a built-in smartshunt which measures the overall current flow from/to the batteries.
But until then I agree it’s better to add the shunt yourself and not rely on the calculation by the GX device.
Most managed Lithium batteries are connected with CAN bus, so a additional shunt isn´t nessary
Easysolar and MP GX are entry-level models for customers who do not want to assemble the system themselves.
Even though the thread is a bit older, I’d like to add a few things, that I recently noticed about the use of the internal battery monitor:
As fas as I understand and see, it is not a setting, but something automatic, that happens, as soon as the connected MPPT is a victron device and connected to the gx device (which is the case for an easysolar 2 gx). The above linked manual mentions an indicator on the system status page, to reflect this, but I could not find the respective page on the new UI (anybody else maybe?). Cant say much about the accuracy either, but it is enough for us. No need for a shunt at all. The setup seems to have one limitation/bug? though: out of habit I first activated the “show DC loads” option. As soon as this is activated, the energyflow into the battery is not shown correctly anymore (even without any actual DC load). The numbers reported to VRM dont add up anymore, so you might end up with lots of solar production, but the system still shows, that the battery is drained. So dont activate that option, if you want to use the internal battery monitor. Please correct me, if any of this is incorrect.
I ultimately decided not to buy an Easysolar II GX, but to go for a Multi RS Solar instead. It doesn’t have a built-in GX, but I found the GX in the Easysolar too limited compared with a proper Cerbo. Besides, the Multi RS Solar is a more modern version of the Multi II (and therefore of the Easysolar too): no more heavy and sometimes noisy transformer, no VE.Bus but fully VE.Can, and it’s also cheaper while offering better performance: