DESS not charging the battery. Ignoring the plan
Hi!
DESS ignores its own forcast to charge from Grid. FYI, the hours from 12-15 was also marked for forcasted Grid to Battery, but as seen in the image, no charging was done. It only idles instead of charging. DESS is in trade mode. Does anyone know how I can fix this? There is no limits that hinders the system to charge.
Thanks for any help!
I can see that the scheduler is sending your system a “grid2battery” restriction past 2 days from 6 to 22? May it be possible that you have configured that in your DESS Settings?
Thank you for reaching out! That sounds strange, I have no idea where I can find that setting. Could you point me in the right direction? Tried setting a property with node-red now, but not sure if this is the case.
The Strange thing is that the 6-22 interval correlates very well with the differentiated pricing I have set up in DESS. On weekdays the price is higher between 6-22.
I really appreciate you helping me in the right direciton.
when you edit the “Battery Settings”, click on advanced at the end, there you can configure some restrictions and as well times for it:
But - no matter if battery setting related or price-related it is super strange that the energy flows outline a purchase from grid, but the scheduler sends a restriction.
Thanks. I just checked. I have no restrictions in the settings. I see its scheduled charge from grid in about 2 hours. Was hoping it actually will charge today. Will report back. Really hoping to find the cause for this behavior. The planed charging/discharging plan looks spot on.
I see that it still ignores the schedule, but I really have no clue why.
I have also tried this monster to see if it has any effect… But still not seeing any charging. Will check back next hour.
When a new hour started, it just reverted back to Grid to battery restricted.
If I then run the this again, the system starts to charge from grid…
Impossible for me to understand why this is happening.
I cannot see any obvious reason as well. I will forward this to the scheduler team. I can see a 8-22h Grid2Bat Restriction today as well - but at the same time target-socs that “indicate charging”.
(And then your system will give the restriction precedence as it should do)
Doesn’t fit together, there is something going wrong somewhere.
I got it:
There is a “rule” that puts a grid2 battery restriction on the MOST EXPENSIVE hour.
And this in your case this is the 6-22 range.
As a workaround:
Select 1 hour of the day, where you for sure won’t buy, probably 8-9 or 19-20 when it is “main-sell-time” - and increase the buy-price there by a tiny amount.
Then, only that hour will be blocked.
Thank you so much!
I have tested this solution for a few days now, and. can confirm that this works out!
Really appreciate your help :smiley: