I have all loads critical. I use one Fronius (12.5kW) which is connected to AC IN1 of the Quattro (3*48/5000/70) and a second Fronius (12.5kW) which is connected to AC OUT1. I have a question, can I get 25kW on the AC OUT output of my Quattro or do I have to necessarily connect part of the load (12.5kW) to the first Fronius bypassing the Quatrro?
It depends on your overall system.
Inverters and Batteries need to be able to fullfill the factor 1 rule. If they do, you can hook up 200 kW to ac out
https://www.victronenergy.com/live/ac_coupling:start
Ah, you don’t want to reallocate the inverter, just use the power connected to ac in on ac out.
Yes, that works, the power from ac in will be passed through, as if it is coming from grid.
Thank you very much! I hear you.