Victron and Fronius recomend a PV array+inverter no mroe than 75-80% of the Victron inverter size. (per their advanced webinar). So in my system 3x Multiplus II 48/15000 , I should have a PV inverter with no more than peak 36 KW. So I’m thinking to go with a Fronius Symo 17.5-3-m which has peak 26kw I believe AC output. And will match up with my 22 KW of panels.
No, I’m speaking about storage size as does vicrtron, which isn’t exclusive of what you’re saying (my bank has a 1040 amp nominal discharge current and higher peak)
3.2 Lithium batteries
1,5 kWp installed AC PV power requires 4.8 kWh of battery storage:
100 Ah at 48 Vdc
200 Ah at 24 Vdc
400 Ah at 12 Vdc
Each additional 1.5 kWp of AC PV will require an additional proportional 4.8 kWh increase in battery storage.
And I am speaking from experience.
Size the bank for the discharge current as per the inverter manual. If you have already fulfilled that
Once the base is good. Size the AC PV that can be supported by the inverter system. The bank has to be able to sink overshoot production/sudden discharge without collapsing the system.
Some batteries have a 1.5 or 2C discharge so now storage size also comes into play - hence the Victron documentation - they wont have the capacity to since the kWatts