I am going to installed a Orion-TR DC/DC charger to supplement the solar charging I’m doing with my Victron MPPT. I have a BMV-712 in place and it appears that I can use the relay on it to control the Orion so it turns on and off and needed. Looking at the manual is shows the remote H pin of the Orion connecting to the relay on the BMV but it doesn’t show where exactly. Doing some digging around, I came across the following instructions but would like to get some confirmation from the experts here. I should mention this will be in a vehicle. So I really don’t want the Orion running unless the vehicle is running. Does this look right?
Step 1: Wire the BMV-712 relay to the Orion-TR
The BMV’s built-in relay is a low-current switch that cannot handle the high amperage of the Orion-TR, so it will only be used to toggle the Orion’s remote on/off feature.
-
Locate the remote on/off terminals on the Orion-TR. These are typically marked with an “L” and an “H” pin or have a removable green terminal block. A wire bridge is installed on the terminal block by default and must be removed.
-
Connect the BMV relay to the Orion-TR remote on/off terminals.
- Connect the BMV-712’s COM (Common) relay terminal to the Orion’s remote on/off H pin.
• • Connect the BMV’s NO (Normally Open) relay terminal to the Orion’s remote on/off L pin.