Connecting the Multiplus 3000 to a BMS 12/200 via aux 1 and tsense port

According to this wire diagram:

you can use inverting remote on/off cables from the t sense port and the aux1 port to connect to the load and charge cut off on the bms. it says you have to upload these settings. does anyone know how to do this via the victron connect app? do I need different software?

You need to do this with a laptop and the VE configure software.
You need to load the 2 signal BMS assistant into the Multi, and follow the configuration settings.
Once done make sure that you send the modified settings to the Multi.
Software is free download from the Victron site.

The assistant has several variables and it’s not clear to me what I need those to be for each channel, “open” or “closed” to activate the allow to charge and the allow to discharge functions? Why doesn’t it say high or low, like the BMS?

There is the contact type NO/normally open or NC/normally closed.

That is what this means. Open is a normally open contact; closed is a normally closed contact.

Naturally, the normally closed contact is used for shutdown: if a wire breaks, the system shuts down and the fault is detected.

The BMS inputs from the inverter are designed to come from isolated relay contacts, rather than logic level signals. Hence the terminology is “open” or “Closed”. The inverter provides a +12V output, and a sensing input that has a pull down resistor to the inverter ground.