Connecting 2 Victron 150/70s to a bank of 2 batteries

I have two Victron 150/70s, each with four panels. I have two 48 V, 100 A batteries connected in parallel. One of them is set as the Master. I don’t have a busbar. My question is: should I connect both Victrons to the Master battery, or connect one to each battery to balance the loads better?

The batteries are connected to each other though?

You can basically cross connect them.
Mppt 1 negative on one battery, the positive on the other.
Mppt 2 positive of the battery (mppt 1 negative is on) and negative on the other.

Make sure your battery bank inter links are decent

That way if they aren’t producing the same the current will share over both batteries.

Most ideally you do want a bus bar

Yes. The batteries are connected to each other, and their cables are the same gauge and length. They’re using the factory cables. What could happen if I connect both controllers to the same battery—the master, the one connected to the inverter? My first idea was to connect everything to the master battery (controllers + inverter).

Just chiming in here - diagonal connection is best, otherwise the inverter load will not be split evenly across the batteries, and the master will wear out faster. Charging, the second battery will not get an even charge. So over time, they will wear unevenly and there will be a difference in capacity.

That’s why the best set up is diagonal as LX described.

One will be charged faster than the other and possibly undercharged.

It is not the best way to take care of them.

Keep to the diagonal connection. See the manual below

It is less than ideal. (Think of the heat on the terminals) You can connect to the inverter posts but if you are lugs stacking be careful they are sitting flat.
The other will have to be diagonally connected over the bank.

A picture is worth 1000 words. Would you mind sharing a photo of your set up?

I still need to connect the controller cables to the batteries. I’ve got it set up like this for now until I find the best option. Victron 1 connected to Battery 1 (Master). Victron 2 connected to Battery 2. Inverter connected to Battery 1.

Are the fans blowing down?
It might be better to blow it up - hot air rises and all that. No point wasting power fighting physics.

Will be interesting to see what your voltage drop is over the battery cable on the mppts. If you are able revise them to a larger gauge. If you are pressing them hard the cable heating will be adding to the heat issue you have added the fans to reduce. And use double insulated cable

What size is the inverter?

This way there is not too many lugs in a stack
And you will be current sharing across the bank

Or the alternative, which was the one suggested earlier.

Please don’t use yellow-green wires for anything other than earthing, etc.

Read through Wiring Unlimited.

Take a look at the Lynx busbar. You can add fuses to the Power In, or use the Distributor directly.

There should be Mega fuses for 58V and 70/80A.

And install a battery switch in the positive line.