I want to connect a 4S 4P array of 16 JA Solar 440W panels forming a single string (153.6V, 56A) to two SmartSolar 250/100 charge controllers with inputs in parallel. On the community I have found both positive and negative comments about using a single string into paralleled controller inputs. One comment mentions the need to have the controllers in a master/slave configuration. Can someone point me to the documentation for doing this? I don’t see anything in the controller manual and I haven’t managed to find a manual on networking these components on the Victron site.
FYI the reason for doing this configuration is that I am upgrading an existing PV string, the old PV (2KW) is far from the house and has a single pair of 1/0 AWG wires for output. That feeds an old Midnite controller. The system has a second string (4KW) which feeds a SmartSolar 250/100 Ve-can. The outputs of the two controllers are paralleled on the battery bus (home-built LFP 42KWH). Works well, but time to replace ancient PV. In the upgrade all 3 Victron controllers will have the outputs paralleled on the battery bus. I’ve read comments that the controllers with paralleled outputs will fight, but Midnite plus Victron has worked well for me, so I’m hoping that multiple Victrons will work as well.
You cannot put mppt’s inputs in parallel. They may not share a common set of panels.
There have never been positive comments about doing this, please don’t try.
This is clearly documented and several existing topics on this subject as well.
Master/slave is for smartnetworking (bluetooth) comms and which will run the charge algorithms (also in the manual), not about a parallel config.
The search option at the top will show similar topics:
Multiple mppt’s, each with their own panels, in parallel on the DC bus with coordinated charging is not a problem. You can use smart networking to coordinate charging, in the absence of a GX, but ideally you would use a GX device to manage this.
The issue is solely sharing the same panels between chargers.
If i understood correctly, you got a 4S3P string already connected to the existing 250/100, while a 4S1P string is connected to the Midnite MPPT? At least thats what i can read between the lines, 16x 440W is 7kW rather than the 6kW you mentioned, so there might be some misunderstanding.
You would need to know the exact panel type to be sure, but based on the info given the Midnite MPPT could be exchanged by a 250/60. Giving you two strings, each on its own MPPT.
From there you can then decide if you want to use VE.smart in order to synchronize the charge behaviour, or not. If you have a GX already, then you should rather use a VE.direct (or VE.Can) cable to connect the MPPTs to that instead.