Batteries not discharging

System has been running all ok but today IVe noticed the batteries don’t want to discharge much and the solar doesn’t peak like it used to. Used to hit 3200w.

Running a multiplus 2 24/3000 with pylontech batteries.

Batteries are fully charged.

When I put a load on say a heater the grid doesn’t want to fall under 450w ish, it doesn’t want to discharge the battery or pull extra from the panels. For example at the moment I am using 2120w with 1072w from the panels and still pulling 1090w from the grid, batteries are at idle. Normally the grid works it way down to 45w and the panels usually cope (we have a sunny day).

I noticed that in the menu it shows max inverter power is 1000w and Lindt inverter power is on.

Should this be the case. If so haven’t a clue how it has changed itself.

Those are settings that are off by default and can only be enabled by manual intervention. It will limit PV and battery use for loads.

1 Like

Thanks.

So for for a multiplus 2 24/3000 should it be set to 3000w and limit inverter off?

I have emailed the installer to. They did do a reconfiguration to it last month and wondered if they changed it.

IVe just toggled the limit inverter power off and all seems to work now how it used to

Thanks.

I think I may have accidentally toggled to limit a few days ago when I was sorting out my scheduled charging.

Thank you