Can the Lynx Distributor take 95mm2 Cables, which i believe is some 18mm in diameter.
Input is not an issue but i need to run these huge cables from the distributor to the Inverter.
Can the Lynx Distributor take 95mm2 Cables, which i believe is some 18mm in diameter.
Input is not an issue but i need to run these huge cables from the distributor to the Inverter.
Good day and welcome to the forums! Did a quick measurement for you, at the smallest part it is about 24mm. A standard 95mm is at most about 18 or 19mm I believe? More than enough space.
Hi Jacques,
Thank you for taking the time to measure the apertures and confirming all will be fine.
I did search the online manuals but couldn’t find the sizes anywhere.
Much appreciated.
This helps me too, as I plan to run three 95mm² wires from my battery modules to the Lynx. My Lynx is the M8 version but that shouldn’t matter.
M8 model is fine as i have two 95mm2 in mine only issue was the lugs had to be shaved down ie the rounded edge so that it could accomidate the mega fuse if you look at my post installing 95mm2 cable you will see the picture of the lug shaved to accomidate the mega fuse
Hi Daza,
I will have a look shortly, Thank You
I regularly use 4/0 AWG wich is around 107mm2. It works but pushes the limits of the Lynx. If I don’t get my cables and lugs very cleanly installed the black tabs that separate the negative from the positive cables can be forced off and the lid can be difficult to close. Just proceed with care and you should be fine.
Thank you for your reply.
Noted. I already tried the options. I had to shave the lugs a bit but my 95mm² otherwise fits. Thanks all.