I have two multis in parallel with each multi limited to 4A. Remote Console states Generator limit 8A, but Victron Connect App states 12A… is this a bug?. I tend to believe the remote console, when I use my MK3 device, I can see both multis are set to 4A…
Yes, the total input current limit is twice what is set on each multi.
Victron connect app must have an error…
There are two places in VictronConnect where you can see the AC input current limit, on the overview page and on the settings page.
The value shown on the overview page is the same one displayed on the remote console. This current limit is the one actually applied when “Overruled by remote” is enabled in the settings page.
Does that system have the Peak Shaving feature enabled? If so, there’s a bug where, in some cases, the wrong current value may be displayed when Peak Shaving is active. This only affects the displayed value.
Thanks for your response!
Do these images help describe my problem?. Overruled by remote is disabled as this is a ‘static’ system, bolted onto my shed’s wall and it’s recommended for my solution… ![]()