I understand your explanation and this is the way i intend to set ac_ignore with assistants but…
If i set the “general flag” as the “relay” to use ac_ignore then ac_ignore works but how do i then make an actual relay (primary programmabe relay) also switch on ac_ignore?
So what i would like to achieve with the image below is:
ignore ac in
switch the primary programmable relay on the same conditions as ignore ac in (this is needed to shut down my solar inverter, i don’t want to inject into the grid)
Can someone comment on this? thanks!
I think this should work, can anyone comment on this?
On is always priority over off. So if any on is triggered the offs will be ignored even if conditions are met.
What i have found easier to get right is use an aux or temp input to set the open and close of the primary relay and (wire it to) use the GX relay (assigned as a generator start stop) then put all the load and soc conditions in there.
I guess that is if you aren’t using it to start an actual generator