We are currently running some tests with two Quattro units that we want to operate in parallel before installing them onboard.
One of the tests we carried out raised the following question:
We noticed that when we connect the AC outputs of both Quattros together and then disconnect the AC input breakers of the Master or the Slave, the system keeps running without changing state.
For example, if both Quattros are charging the batteries and one of them loses its AC input, the system continues running as if nothing happened — it does not switch to “inverting.” More surprisingly, the Quattro without AC input keeps charging the batteries, because it receives power from the output of the Quattro that still has an active AC input.
I would like to know:
Is this behavior normal?
Is it expected that the Quattro without AC input produces a strange electrical noise in this situation?
We’ve seen this a bunch of times with our Quattro 10k’s as well. LOM type B.
My assumption is that it’s difficult to properly detect loss of grid (by frequency shifting) when there’s still a path to the grid via the one inverter still connected to the grid.
Also, I believe only the phase master does LOM detection.