We have 5 MPPT chargers connected in the same point to our house bank of Lithium 12 V 750 Ah.
Two of the chargers indicates 14,2-14,3 Volt and they charge in abs and float. At the same time the other 3 chargers indicates a voltage of 13,7 Volt and charge in bulk mode. The difference is about 0,5 V higher for the two MPPTs.
The BMV indicates the same voltage as the 3 other MPPTs.
I have tried to make a reset to default but that didn’t help.
Get a multimeter and when charging measure the voltage on each MPPT’s battery terminals. Then you will know if the voltages are different or if it is a measurement error. Simple basic electrical troubleshooting rather than thinking it is a settings issue.
I made some measurements on the bat. side on the MPPT and for three of those it was between 13,57 V and 13,74 V, the two others was 14,06 V and 14,07 V. On the batteri connection it 13,72 V. At the same time BMV indicates 13,26 V, and the batteries between 13,20 V and 13,22 V. See enclosed photo.