My problem is, when device (like hob) which I have on the phase3 will switch on - complete victron system is confused. It’s trying to send energy to phase1, where is installed and makes a feed in :
Please describe you system a bit better.
What components do you have exactly?
Is the Fronius 1-phase or 3-phase? If 1-phase at which phase is it connected?
Looks like you also have a MPPT in your system.
Is AC and DC feed-in activated?
The ET340 is not recommended as grid meter, you should use an EM540 there:
It’s one phase system. All is on the phase1. Multiplus II, On the ac input of multiplus is Fronius and there is also mppt + battery pylontech.
Grid measurement is done via ET340 as described
AC and DC feed-in isn’t activated: