OH ok i see now. Makes sense.
Thing is I am trying to over panel for the dark wet months. So if the calculator rejects a certain layout because of being over 130% I wish it would just say that instead of just outright rejecting it.
As it stands, until I come into this community and ask a ton of questions I dont know why the proposed string is being rejected. As you point out it is most probably because of being over 130% - OK I accept that the calculator is rejecting a proposed string because a parameter is going over its limit.
But it still doesn’t answer my question about how many amps can I design up to when using the /100 amp rating on a Victron Mppt. How much headroom do I need to leave for Isc input when using a 150/100 or a 250/100? Is it just the heat rating I need to calculate because the amps RISE a little with heat? Is there no need to think about cold temps when thinking about how much headroom I should leave for the amp limit input?
Ie, should I design around 56A input for the 70A Isc limit thereby leaving a 25% margin for headroom ? Can I design for 65A input to the 250/100 ? Can I design right up to 70A of input to the /100 series mppt’s? I cant find any clear statement on this anywhere. I dont want to setup a string of panels that is unsafe for the Mppt.
Sure I can follow the calculator - but that seems to be limiting on the 130% oversizing - which is fine from a certain perspective - ie the waste angle you alluded too - but if I want to oversize beyond that for reasons that make sense to me I want to make sure I dont push too many amps into input side of the mppt. I know the hard limit is 70A but do i leave some headroom on Amps or not ? Using the calculator I cant find that amp numerical figure that i must not go beyond while leaving some headroom - should I just assume I can go up to the number of amps that the heat calcs allow while respecting the hard 70A input limit and leave it at that ?
Re your calc : (4s4p) 16 x 580 = 9280w. (9280w ÷ 48v = 193A) - 1st thing is we need to calculate for 51v not 48v - So 182A. The LFP battery would never be at 48v. So this reduces the amps a little - not a huge amount for sure but it all adds up. Also your figures are at STC which we wont hit for all the known reasons. I am in an area that is hot while it is also raining. So very heavy overcast weather in between rain events while ambient temps are in the 30’s. It may go several days without rain but always very overcast and hot. So never going to hit STC in those conditions so never going to see 182A at that time of the year. I am not interested in trying to harvest more all the time throughout the year , just interested in harvesting more in certain times of the year. So i have to over panel for that.
Getting a bit off topic but one thought I had was to go ahead and build out a 4S4Psetup. When building a combiner box for this array, set it up such that I can turn OFF the 4th string in the clear sky sunny times of the year so that the extreme over paneling does not come into play at that time of year and then turn that breaker to the 4th string ON in Dec/Jan/Feb when we are struggling to make decent PV. That would solve the problem - is this a way forward that would not break any rules etc? Sure it is a manual thing - having to turn a breaker on and off twice a year - but it would solve the problem.
So with regards to amps - the hard limit is 70A input. The outgoing battery charging amps is up to 100A. Is the over paneling case I am putting forward, which is causing the amps presented from the panels to the battery charger in the Mppt to be well over 100 amps, the problem ? Is pushing the charging amps side of things too hard going to cause the Mppt to overheat ?
Not trying to flog a dead horse here, just want to understand it better.