XS1400 DC/DC Mode – Premature Shutdown due to In-rush Currents
We are currently utilizing the XS1400 in Power DC/DC Mode and are encountering issues with the overcurrent protection sensitivity.
Technical Specifications:
  • Input Voltage: 24 VDC
  • Output Voltage: 12 VDC (Max. 20 A)
  • Load Setup: The output is connected to a relay box controlling various peripherals.
Issue Description:
While the XS1400 operates reliably under steady-state conditions, the DC/DC output shuts down immediately as soon as a relay in the external box closes. Although the static load is relatively small (approx. 1 A), the transient in-rush current during the switching process triggers the device’s safety cutoff. Tests with an electronic load system have confirmed this behavior.
Troubleshooting Performed:
We have attempted to resolve the issue via the app by adjusting various parameters, including increasing the maximum current limit. Unfortunately, these changes have not prevented the shutdown during peak transients.
  1. Is there a specific setting to adjust the sensitivity or response time of the overcurrent protection to tolerate short-term in-rush peaks?
  2. Can the device be configured to a “Constant Current” mode instead of a hard shutdown when a peak is detected?
  3. Are there recommended software configurations to better handle inductive or capacitive loads in DC/DC mode?
Thank you in advance for your technical assistance.
I am having the same exact issue on a vessel with the Orion Xs 1400 set up in Power Supply mode (12vdc supply and 24vdc output). Every time we energize a circuit breaker connected to any electronics, the system shuts down and resets. We have dropped the low voltage shut-down to 9vdc and it will still shut down. Has there been any updates or fixes for this found yet?