I’ve recently setup my first Multiplus2 system.
My setup is: MP2 3kva, CerboGX, Lynx Distributor, BlueSea 9001E, MPPT 100/50
DIY Battery with 24V 314AH, JK Inverter BMS
Using a decent clamp-meter (KAIWEETS HT206D) set to Maximum amp mode, I have not been able to detect any inrush. I monitored the main battery positive during initial connection, and power-on. I’ve seen at most 1 amp draw, which was likely going to the Cerbo & MPPT.
Does the MP2 actually have an inrush current? Does it pre-charge itself?
I would guess it would charge capacitors:
At initial power-on
At soft-switch turn to “anything but off”
I would guess it would not charge capacitors:
When Battery leads are connected, but physical switch is Off.
But I do not seem to be seeing any kind of inrush current. Perhaps my clamp-meter isn’t capable?
My best guess is the MPPT is charging the inverter. Does anyone know how many watts are needed to charge it?
OGPS
(Ed @ Off-Grid Power Systems - offgridps.com)
3
Yes, it has a very large in-rush current. And yes, if your MPPT is enabled it will pre-charge the capacitors in the inverter. An MPPT is one way to accomplish pre-charge because it is inherently current-limiting device. However, that’s only useful during the day time
Get a resistor of suitable size and a momentary switch. Mount the switch to the inverter or panel it’s installed on. Press button for 5 seconds and you’re done. The caps will discharge in short order so the pre-charge circuit is nice so you aren’t switching under load (inrush) and you will extend the life of the main switch contacts as well as the caps.