Hi all,
Over the past month i have been testing my new victron setup. A little context:
- Single phase Victron 6k5
- 3 Phase house
- Grid meter: VM-3P75CT via ethernet
- Induction plate: etna AKI680ZT
- This is a 2-phase (7.4kW) cooktop but wired 3 phase, 2 pucks are on phase 1 (same as victron AC-in) and 2 pucks are on phase 2, 3 is unused
- ESS compensating all loads.
- Ping from GX to Energy meter is 1.2ms
All “normal user” loads are on the AC out of the 6k5. Heatpump, Induction plate, EV Charger, are on the AC in side.
What i observed (like many of you did before) is that the 6k5 is unable to compensate on the AC side for the cooktop
Finding 1
When the cooktop is set to a medium-high setting (level 7), the PWM pulses are roughly 4 to 5 seconds long, pulling around 1250W:
As seen in the measurement above (i polled the energy meter at 10hz)
- Red areas (Grid Import): The cooktop switches on instantly. The ESS starts to ramp up, but takes several seconds to reach the target. During this time, I am buying power from the grid.
- Green areas (Grid Export): Just as the inverter reaches the 1250W target, the cooktop switches off. The inverter now blasts -1200W peak into the grid before it manages to ramp down.
I did a little financial impact calculation: Despite the terrible efficiency, the battery still covers about 60% of the energy needed for this cooking session.
Finding 2:
Things get worse on lower settings (level 4). The pulses still hit ~1250W, but they only last for about 1 to 2 seconds.
Because the pulse is so short, the ESS barely has time to start ramping up before the cooktop turns off again. The result? Almost 100% of the required energy is imported directly from the grid, rendering the home battery effectively useless for this specific cooking session.
I used the 10Hz data to calculate the speed at which the inverter adapts its output based on the grid meter data.
- Ramp-up speed: ~309 Watts / second
- Ramp-down speed: ~358 Watts / second
To compensate for a 1250W induction pulse, the Multiplus needs 4 seconds to reach the target. This kind off explains why short pulses (level 4) are completely missed, and medium pulses (level 7) cause massive overshoots.
The AC-Out Comparison
To rule out hardware limitations of the inverter itself, I turned on my Oven (3kW) on the AC-Out side. The compensation was instantaneous (fully compensated in 200ms). The inverter has the physical capability to deliver the sudden power surge (it should be in case of LOM), but it refuses to do so when compensating a load on AC-In via the grid meter.
My temporary workaround
As these pulses are easily detected (not much devices pulse like this, but my espresso machine also does it a bit too). I run a node red flow that will set the Self consumption from battery from All system loads to Only Critical loads When this behavior happens. Although it’s financially better to have this overcompensating behavior (it still covers some of the load). It puts extra stress on the inverter. Result:
And the inverter stays quiet. But i rather have a better compensation.
My Questions for you / Victron R&D
The 10Hz VM-3P75CT meter is incredibly fast, so the bottleneck seems to be either the VE.Bus communication or hardcoded firmware limits.
-
Is the ~310 W/s ramp-rate limit a hardcoded restriction forced by European Grid Codes (EN 50549-1) to prevent grid destabilization? My opinion would be that a constant 0 on the meter would be more stable than this kind of pulsating behavior.
-
If this is not a strict grid code limitation, are there any ongoing developments in the “Fast ESS” architecture to safely increase this ramp-rate for internal VE.Bus looping, allowing the system to get closer to AC-Out performance?
Thanks for reading, and I’d love to hear your thoughts on this! (and thanks for all the amazing other topics, they helped me a lot in my journey)