I have marked the missing power of the Multi Rs with red boxes in the diagram. The yellow boxes show how the power of the AC inverters continues to increase
The battery is of course already fully charged at this time. I can’t see any errors in the log that cause the power limitation. The mains voltage reaches 242V at this moment. Actually, it should only be limited at 252V, right?
How can I find out what is happening here? Where can I look?
This is only related to the external victron meter (in my case the vm-3p75ct ). As soon as the external meter is disabled in Victron Connect, the throttling is gone. But we can’t disable the vm-3p75ct grid meter as we would blow out the main fuses of our grid.
I tried to switch off “Support of energy Meters” in all 3 Multi RS" Settings but it did not change anything. max 20A feed in and if the ac inverters reach this, die Multi RS will stop producing energy at all.
Edit: I think the reason is that my AC Inveters are currently conncted to AC OUT. So the energy is counted. I will switch them to AC IN, disconnect the Meter and will try again. I will keep you updated…
Even if the RS is only supplying a couple of watts if the SolarEdge PV inverter is doing all the rest?
So it must be some software bug / hidden setting that limits the total grid feed in to 5kW.
Sorry, maybe I am missing something…
How much should it feed-in continuously, at about 40*C, the normal/usual operating temperature?
Isn’t it the Multi RS a 5kW inverter?
In this 5kW all energy from AC Inverters on this phase is included, this is the software problem we are facing. A workaround is that the Multi RS does not know about the ac inverters. Put them on AC IN and disconnect Meter, for the heavy sun hours…
Or just charge the battery at these times..
The problem is that I cannot disable the external meter as then the power would go over 11kW per phase, blowing out my main fuses.
My SolarEdge PV inverter on AC IN is able to provide 18kW in total, so 6kW per phase, add another 5kW from the Multi RS and the fuses go boom.
But if I enable the external meter, the feed in is limited to 5kW per phase only.
Sorry, maybe I am missing something…
How much should it feed-in continuously, at about 40*C, the normal/usual operating temperature?
Isn’t it the Multi RS a 5kW inverter?
The Multi RS inverters are actually able to provide about 5,6kW of power. It is a 6KVA inverter