Hi All,
We will soon receive our solar system for installation, and before that I would like to confirm with you if you notice anything missing or potentially incorrect in the equipment list below. This way, we can address it before installation.
The system will be installed on a tiled-roof house near the sea (exposed to salty air and wind). The panels will be divided into 2 strings on the south roof.
The Victron equipment and the batteries will be installed in the garage (the garage is only 3 m away from the house, but it’s ~30 m away from south roof panels in terms of going down from the roof to the ground floor and then to the garage with wires + the main electric panel is right under the south roof). We are also considering adding a fire suppression system in the garage to protect the Victron equipment, batteries, and our electric car. Ideally, the system would first disconnect all power before activation.
We would like to confirm:
-
Would a water-based system inevitably damage the Victron devices (inverter, MPPT, Cerbo GX, etc.), even if power is disconnected beforehand?
-
If fully disconnected, is there any chance the equipment could be safely restarted after professional inspection and once fully dried — for example, if only one battery was affected?
Additionally, we would like your advice on alternative fire suppression methods that are safer for electronics, such as:
-
Aerosol-based systems (e.g., Novec 1230, FM-200)
-
Gas-based systems (e.g., CO₂, inert gas)
We want to ensure that the system is protected from fire without risking irreversible damage to the Victron equipment. Could you advise which solution would be most suitable for a garage installation in a residential setting?
Equipment List:
-
Aiko Solar Panel A-MAH72Mw 590W Comet – 10 units (MC4 connectors, silver frame, 1500V, 30mm)
-
Coplanar Roof Structure (Tile-Saver type, Ref. ST_CST_833_05V) – 2 units
-
Victron MultiPlus II 5000VA 48V – 1 unit
-
Victron SmartSolar MPPT RS 450/100 (MC4) – 1 unit
-
Victron Energy Meter VM-3P75CT – 1 unit
-
Victron Cerbo GX MK2 – 1 unit
-
Victron GX Touch 70 – 1 unit
-
Victron GX Touch 70 Wall Mount – 1 unit
-
Victron RJ45 UTP Cable (1.8m) – 2 units
-
Victron VE.Can to CAN-bus BMS Type A Cable (5m) – 1 unit
-
Victron RS485 to USB Interface Cable (5m) – 1 unit
-
Victron Lynx Distributor – 1 unit
-
Victron MEGA Fuse 125A / 80V – 1 unit
-
Victron MEGA Fuse 200A / 80V – 3 units
-
WECO 5K3XP Battery (5.3 kWh each) – 4 units
-
Battery Cable 35mm² (Black/Red) (2m each) – 1 unit each
-
Battery Fuses – 8 units
-
Battery Cable 70mm² Black (4m) – 1 unit
-
Solar Cable (Red + Black) – 1 unit each
-
Ground Cable – 1 unit
-
AC Distribution Board (6 kW) – 1 unit
-
DC Distribution Board (2/2) – 1 unit
-
Galvanized Steel Plate (130x80) – 1 unit
As end users new to Victron systems, we would also like to know what apps and tools are recommended for troubleshooting, performance optimization, and safety checks after installation.
We have found the following suggestions but would appreciate confirmation or improvements:
-
Apps: VictronConnect, VRM Portal, WECO BMS app
-
Hardware tools: Clamp meter, insulation tester, thermal camera, PV string tester
-
Software/config: VE.Configure, VRM Alerts
What tests should we requests done to prove the system is well set?
We also have a TV antenna on the roof, but we are not sure if it is properly grounded (to be confirmed). Currently, there is no lightning rod on the house, and it appears that neighboring houses do not have one either. With the addition of solar panels, so more metallic surfaces on the roof, we are concerned that the roof may now attract lightning more strongly. Could you advise if additional grounding or lightning protection is recommended for our setup?
Thank you very much for your support!!!