Victron Orion xs 50a bulk time setting missing, stays in absorption mode

Newly installed Orion xs 50a stays in absorption mode and does not have bulk timer setting.

I have a new xs Orion 50a charger. Previously I had a 20a competitor. I upgraded wiring for 50a.
I installed 20a back to verify wiring worked fine. It did. Configuration is truck to 15 foot teardrop camper.

After installing new unit:
Upgraded to latest firmware.
Set to lithium battery manufacturer recommended setting 14.6 v no float. Batteries are 2 12v 150ah wired in parallel. Both brand new.

The unit only goes goes into absorption mode.
Working with distributor I discharged batteries to
30% them charged to 50%, them 80% using 120v Victron lithium charger.

Same result, but the current varies. At 30% it pulled 30a but stayed in absorption mode. This was true at all SOC’s (charged via 120v charger up a point where current starts decreasing to levels you would expect in absorption mode.

The manual references a bulk charge time setting, which I wanted to verify /try setting as a troubleshooting option. I do not have this setting.

Online I found a picture a guy posted from 5 months ago. I do not have this setting option.


Picture with setting

Picture with my setting option

(Not sure that I will stay with 14.6v, but that is not relevant to this question and changing it doesn’t change my issue).

Thinking this might be related to my issue.
Thank you
Jim

Didn’t seem to get the correct picture of my settings
Trying again

What type/brand of batteries?

Any loads connected to batteries/charger ?

Measure voltage at xs and batteries, check voltage difference.

Hi
Try enable float voltage, then i think it works.

Eco-worthy batteries.
Voltages are same at battery, camper connector, and battery when charger turned off.
Have varied between load and no load on batteries

When turned on charger is 14.6 because it is absorption mode (voltage constant) while delivering up to 30a.

From manual:

Appreciate the help

Thank you

I have tried various float voltage settings, off, lowered, raised etc. . Bulk setting/absorption mode never changed.

Good idea though

Thank you

(Figuring put how to post correctly)

Ludo, did you note the pics? The bulk time setting is grayed out and bulk time cannot be set. Whether hooked to batteries or not. Any ideas on that? Firmware issue?

Thank you

![image|231x500](upload://fzTQoD2a2lN0KGVWyufRpBtlW4d.jpeg

Has anyone experienced this screen in a working environment hooked up to Lithium mode?

Bulk is grayed out
There is no bulk duration setting

From manual:

Hi

The bulk time in the manual is the maximum absorbtion time in settings.

Sten,
Interesting. The manual shows two separate settings. But you may be correct. Thank you for the response.