I updated my Multiplus II GX 5k inverter to the Victron MultiPlus-II 48/6k5/100-50 at the start of the summer as I will need 100amp charging to take advatage of the cheap electricity from Octopus. As I have Solar I haven’t needed to charge the batteries from the grid as there has been enough Solar to top the batteries up on a daily basis.
Today Octopus had a free 1 hour electricity slot so I set up a timed slot to take advantage., additionally it was also sunny so I was getting around 2.8Kw from solar. The overall charging was around 60amp not 100amp. I also tries changing the batteries to Keep batteries charged and got the same result.
I have been through the configuration and can’t find anything that looks misconfigured.
Shore Limit 63amp overruled by remote enabled
Grid UK G98/1 amendment 6
Charger 100 amp
Assistants ESS (Energy Storage System)
ESS external meter
Mode Optimixed without Battery Life
Limit inverter power off
Battery monitor Automatic
Auoselected Pylontech batter on CAN-bus
Battery modules 7
Installed / Available capacity 570Ah
Charge Voltage Limit (CVL) 53.20V
Charge Current Limit (CCL) 335A
Discharge Current Limit (DCL) 365A
The low charging isn’t a problem at the moment as there is time to charge the batteries overnight. The problem will be apparent when winter draws in.
Help would be greatly appreciated (as alsways).
Steve W