We’ve just gone away for a few days and have been able to confirm that our ESS does not behave as expected when the battery fills up but it’s still sunny. The AC PV continues exporting but the DC side stops when the battery gets full.
System:
Multiplus II 5kW
2.9kWp AC-coupled PV
4.2kWp DC-coupled PV into smartsolar 250/70
16kWh LFP battery (Fogstar with Seplos BMS)
We are using ESS and DVCC.
The issue seems to be the same as this post (another AC+DC+batt ESS system):
Problem with SmartSolar MPPT operation which didn’t reach a conclusion
ESS settings:
AC coupled PV - feed in excess
DC coupled PV - feed in excess
(we also have a feed-in limit of 5kW)
Grid metering ‘Inverter/charger’ (CT clamp plugged in)
DVCC settings:
Battery connected over CAN
SVS, STS and SCS are on.
So the batt charges to 100% as you would expect, but then the MPPT essentially turns off, (70-150W), rather than continuing to export the ~2kW it’s capable of with current sunshine. I can manually change the setpoint to -3.6kW and then the MPPT wakes up and goes to ~2kW, so we export ~3.5kW in total, and the battery stays at ~99%, because input and output are more-or-less balanced.
I was hoping that “DC coupled PV - feed in excess” meant this would happen automatically, as it does on the AC-side.
The topology is http://wookware.org/files/DC-coupled-parallel.svg
So the AC-PV is not through the multiplusII, but the multiplusII is running with a CT clamp on the exit from the building.
System setup:
AC Input 1: Grid
AC Input 2: Not available
Position of AC loads: AC input & output
Batt Monitor: BMS16S200A-SP112 on CAN-bus
Has DC system: No
The BMS does correctly turn down the max charge current from 180A to 10A at 98.5% then to 0A when the 1st cell reaches 3.60V, so that’s all working as expected.
I must admit that I’m not quite sure how the DC current/voltage control is done when the system wants the MPPT to send power straight to the Multiplus but not to the battery. The voltage still has to be controlled to be nice to the battery, but presumably the MPII draws current and the MPPT responds. Which box is in control of what out of the batt+BMS, cerboGX, MPII and MPPT when doing this balancing act of not battery overvolting, but not really discharging either, whilst shifting several kW from DC to AC sides? It works fine when I change the setpoint manually and the export is recorded as ‘Solar to Grid’ rather than ‘Solar to battery’ on the VRM charts so they system knows what’s going on.
What do I need to change to make the MPPT keep supplying power and the MPII move to exporting any available DC PV after the battery is full?