Victron energy Bluesolar Charge Controller MPPT 250|100, Charging issue through Solar

Hii,

I have a Victron energy Bluesolar Charge Controller MPPT 250|100 - Tr VE CAN.

I connect the solar panel input to the controller and output from the controller connected to the battery pack system. Solar input which iam getting is 98V and present battery voltage was 50V, both the voltages of solar and battery was showing in the controller screen but current is not flowing, what might be the reasons ?

I cross checked every possibilities, my doubt is, is there any fuse which lies inside the solar charge controller, is because of that it was restricting ?

Most common reason is reversed polarity on the pv side.

Second is the rebulk offset.

You would see 'reason why my charger is off: if there were any other causes.

Hello, thanks for the insights,

  1. Checked the solar connection polarities with the help of Multimeter before connecting to the charge controller.

  2. Couldn’t get the point, what is rebulk-offset and where this setting lies.

  3. It wasn’t showing any error.

For better understanding I’m attaching the few photographs for your reference.

(attachments)

In settings activate expert mode and then it will appear.

Settings

Is yours a smart solar or just the blue solar (no Bluetooth)?

On display it was written as SmartSolar Control. But in the charger, it was written as Bluesolar Charge Controller MPPT 250|100-Tr VE.CAN .

For the identification, I am attaching the picture of the charge controller.

(attachments)

Yeah, I found the expert mode and i turned it ON. Below I am sharing the screenshot of that kindly look into it once.

(attachments)

Change your rebulk offset to as low as it can go. Mine is at 0.4v you can set it as low as 0.1v.

If you choose the lithium profile preset then edit it with the correct voltages it should be fine.

I see it is marked as BMS controled do you have a GX and a lithium battery connected to it?

But if i keep the rebulk-offset was too low might the charger will detect the drop in voltage and will restarts to charge the battery again as the difference was too low, might it will charge frequently.

Re-bulk restart voltage = Float voltage − Re-bulk offset.

If suppose float voltage is 54.6 and Rebulk-offset value is 0.1V
= 54.6-0.1
= 54.5 and charger will start charging again

But if i keep the rebulk-offset was too low might the charger will detect the drop in voltage and will restarts to charge the battery again as the difference was too low, might it will charge frequently.

Re-bulk restart voltage = Float voltage − Re-bulk offset.

If suppose float voltage is 54.6 and Rebulk-offset value is 0.1V
= 54.6-0.1
= 54.5 and charger will start charging again

Is it recommendable to keep the rebulk-offset as low as possible?
My battery chemistry is Lithium ion NMC

Then that is up to you. In your post the battery was down to 50v so clearly the current settings are not great. I am going to ask again though i see equalisation which means a lithium profile was not chosen then edited. Start with that. It removes the equalisation there and a few other things not related and add low temp cut off.

At this point you are really wanting to determine if it is defective or not. So we do need to try to get it to charge.

Not if the bms says no.

The bms control changes things alot here as well. The bms itself may have told the solar not to do anything, which is why i asked about bms control. It it sending a CVL and CCL to the system?
How else is the system programmed? Do you have ESS?

Have no idea on that regarding the CVL and CCL,
No, don’t have ESS.

Can you please guide me how to resolve and diagnosis it and find out the root cause.

Have no idea on that regarding the CVL and CCL,
No, don’t have ESS.

Can you please guide me how to resolve and diagnosis it and find out the root cause.

I was using JK BMS and battery pack capacity was 17kWh.

Have no idea on that regarding the CVL and CCL,
No, don’t have ESS.

Is there any fuse will be there in between the battery and charger? For protection purpose inside the charge controller ?
I was thinking there might be any hardware issue happened inside the controller,

Can you please guide me how to resolve and diagnosis it and find out the root cause.

Is this connected with a can cable to a GX device like a cerbo or ekrano. Is the moot connected to angx device as well?

Yes, from the BMS PCB port one communication cable was going to Cerbo Gx.

For better understanding i had attached the small video of that, please kindly go through it once.

Communication cable from BMD to CerboGx.mp4