I have a Cerbo GX connected to a smart shunt, the generator has its own controller that controls the choke and starts the generator but it only has on-and-off control nothing else so it is controlled through the relay with no feedback as to whether the generator starts successfully, I have added in a digital input that will trigger high if the generator start successfully but there is no way to tell the Cerbo to restart the generator if the digital input is showing the generator is not running when the generator relay control has triggered the generator to be on, and it has failed to start. any help would be greatly appreciated.
If it is controlled through the gen start stop on the gx you can activate the ‘ac not detected at input alarm.’
there is no way through normal interface to try automatically restarting the generator. You would have to look into node red for that