Unexpected low voltage alerts - how to debug?

All,

My system:

  • 1x MP2 48/5000/70-50
  • Lync Shunt
  • Cerbo GX MK2
  • VM-3P75CT
  • 16x LiFePO4, JK-BMS JK-PB2A16S20P
  • Battery Monitor: Lynx Shunt
  • 70mm2 cabling
  • Configured as ESS, with minimal 30% SOC
  • 1x per month, system will be charged to 100% SOC (or more frequent if there is sufficient solar)

I get frequent (multiple times per week) Low Battery Voltage alarms/events reported by MP2.

These events happen when SoC is at 30% (no charging or discharging at all)

I monitor with MQTT/InfluxDB/Grafana the historical data.

Battery voltage is stable at 51.8V when alarm happens - which is pretty normal for 30% SOC

I also store minimum and maximum cell voltage (data from JK-BSM); lowest cell = 3.24V; highest cell = 3.25V; no dips seen.

I realize that I might miss transients….but low battery events do happen when there is no charging/discharging. ESS is configured to maintain 30% SOC, no solar, so no charging & discharging. My Grafana data also confirms this). System works find when charging with 60A / discharging with 30A…so I do not suspect lose connections (all are done with required Nm).

I have looked at lots of historical data; no transient was captured.

During discharge, the voltage drops to 51.4V, but at that time, no low voltage alarms….

Settings:

  • MP2 Low pre-alarm = 50.1V
  • Lynx low battery alarm = 46.6V
  • JK BMS Cell Under Voltage Protection = 3V
  • JK BMS SOC-0% = 3V, SOC-100%=3.45V

Lynx voltages are consistent with MP2; same for JK BMS

MP2 is giving the alarm.

Lynx Alarm State = OK

Any clues? Is there any way to find out what the actual trigger is (which voltage) - too bad that events don’t show this.

I am out of options…

Thanks, Hans

All with latest FW of August 2025.

Usually when it is not under load but under battery idle it can be the battery thinking is needs to power save / sleep.

Ok… but how can I stop this?

Have you set any sleep settings on the JKs?

I have now lowered the Smart Sleep Voltage on the JK BMS…lets see if that changes anything. Thanks.

Please add a screenshot of the ESS assistant settings.

I meant the VE.config ESS assistant settings of the MultiPlus.

I was not 100% sure what you were looking for.

Below are all settings from my MP2. (screenshot & pdf file)

victron.pdf (340.1 KB)

You dynamic curt off at idle is 52.0V.
You state getting low voltage at 51.8V.
You reached low voltage on idle.

OK…thanks a ton…sounds plausible.

I tried to find where I can find these settings via VE.Config to MultiPlus II, but I can’t find any where…Yes, ESS assistant does show these (above screen shot)….but where can I change these?

I also looked around with VictronConnect @ Cerbo, but didn’t find anything.

Google did not point me to any usefull…

Thanks

Hans

I got it resolved. You have to restart the ESS mananger to change the settings….that is not completely obvious :slight_smile: