In the docs for the Multiplus II it links to this doc for the G99 application:
I’m trying to find the ENA number for the G99 application though. https://www.ena-eng.org/ only has data up to 16 March 2024, I’ve searched on https://connect-direct.energynetworks.org/ (which is supposed to be current) but the last Victron inverter that’s been added was the 48/15000 in June 2024.
Does anyone know what system reference to use for a G99 application with a Multiplus II 48/6k5?
@pau1phi11ips Not every product is necessarily going to be submitted to ENA for validation as soon as it is launched and there is already is good choice of certified products. May just be a matter of time as it is also a time consuming and resource intensive exercise and then again it may not be on Victron’s roadmap at this point in time.
@pau1phi11ips Some insight Multiplus UK G98 G99 non-compliance update - VictronEnergy into the compliance assessment mechanism. It would really depend in this case the severity of non-compliance and whether it will require e.g. firmware or even hardware adjustments to comply with likely newer standards as the test results submitted may not reflect all the requirements for certification. My advice has always been to ensure the product is certified before purchase if it is going to be connected to the grid. The next steps decision would be purely an internal one with Victron and it may be worth contacting the regional sales manager on this question.
This is a frustrating one as the ENA Connect Direct shows the unit as being fully type tested against G99 A but still not compliant. Our DNO, with the test docs and this, won’t accept unless the portal shows compliant. I’ve raised a support case with ENA to see what the block is.
Really helpful and came back very quickly. Said that the units have been fully type tested and paperwork submitted, but something is not quite right with the paperwork and so can’t be marked as compliant yet. They confirmed that there is active dialogue between them and Victron about this. No timeframe.
I also spoke to the UK sales rep for Victron and he said that they are working on it but due to summer staff gaps that there were some delays.
Promising from both sides but no specific resolution time yet!
Any chance you could log another support case with ENA to see what the issue is this time?
I tried raising a support case with ENA and frankly the response was useless. They essentially told me they couldn’t provide any details of what the issue was or what needs to be done to resolve it.
So from following up with Victron themselves it appears that the issue is as follows.
The first submission required corrections to the test certificate. These were actioned and the certificate was resubmitted. ENA rejected it as non compliant because those were incorporated via an addendum rather than in the body of the certificate itself. So currently it would appear that the test house need to produce a new certificate with the relevant corrections in line and then submit that.
It seems like a bit of a lottery tbh, a different assessor may have been fine with the addendum, clearly the one Victron got wasn’t.