Hello Jack,
Apologies for the delay in responding. Good to hear your are working on a split phase system also.
Have you had any success with the metering?
We haven’t made any further progress yet at our end. Have a new split project due to commence very soon that involve 20kW+ Solar PV and a 9kW wind turbine that will be installed with 80kWh of battery storage on a typical 100A split phase where we will be using 2 single phase inverters. For it we are planning on using Sunsynk solution instead of Victron, due to the simplicity of wind integration and proven reliability with wind.
72kva is a big split phase system!
On the metering front I’m not sure how the Carlo Gavazzi EM24DINAV53XE1X will work? That model is only 65A Direct Connect?
If the grid supply is 250A you would need a CT model and accompanying CTs. 250/5A.
Also the EM24 is slower at responding. I only use the EM530 meter which is much more responsive and can be configured for most scenarios being CT connection. However I don’t believe it will work split phase.
On the meter voltage, they are specified as 3-phase 400V/415V meter with tolerance. I wouldn’t be comfortable installing outside the rated range on the manufacturer datasheet of 208-480V.
A split phase supply would typically be 480V nominal L-L but wouldn’t be uncommon to exceed 500V.
Ye suits normal for the Utility Grid meter to be Arithmetic method as opposed to vector, treating phases separately. Not sure if Vector DNO meter is available in the UK?
There is a setting within ESS; individual phase should be selected.
A possible reason for a difference in the utility meter and Victron/Carlo Gavazzi reading could be If the Carlo Gavazzi is expecting phases with 120Degree Angle? I’m not sure if that is the case or if it can be configured?
I do notice the manual of the EM530 shows a 2 phase 3 wire configuration but there’s not a lot of detail
If I was implementing a Split Phase Victron ESS, I wouldn’t use the Quattros, instead would consider the Multiplus II models; Which you can connect Victron CTs directly to a master on each phase and thus as they are configured for split phase 180Degrees and measure the voltage reference internally on each phase exclusively, I would like to think the power readings would be correct and this should operate correctly on charge and discharge.
Has anyone tested this?
However I gather the limiting factor on this method is a Victron 100A CT appears to be the only option?
I guess above this power 3-phase is more practical!
I’m not sure on what the solution would be for your setup. Hope you get a solution.