Strange PV production and consumption in VRM early in the morning

Hello Community,

I am seeking some insight into a strange data behavior I’m seeing on my VRM dashboard every morning.

System Setup:

  • GX Device: Ekrano GX (Firmware: v3.80~7 - Release Candidate)

  • Inverter/Charger: 3x MultiPlus-II 48/5000 (Three-phase system)

  • PV Inverter: GoodWe SDT20 (connected as Sunspec PV Inverter via Modbus TCP)

  • Solar Chargers: SmartSolar MPPT RS 450/100 & 450/200 (Firmware v1.27)

  • Grid Meter: VM-3P75CT (Firmware v1.11)

  • Batteries: JK-BMS (via Pylontech driver) and SmartShunt 500A

  • Additional Loads: EM24 Ethernet (Heat pump) & MQTT EV Charger

The Issue:

Every morning, exactly when the first PV production begins and the GoodWe inverter wakes up from its “Deep Sleep” mode, I see a massive, instantaneous peak in both PV Production and Consumption on the VRM Overview.

Observations:

  1. Symmetry: The consumption peak perfectly mirrors the PV peak. This leads me to believe it is a calculation artifact, as the GX device likely assumes the “extra” reported power is being consumed to balance the system logic.

Clean “Advanced” Data: When I look at the individual widgets for the MPPT or the Inverter under the Advanced tab, these peaks are not present. The logged data there looks perfectly normal.

  1. Timing: The issue only occurs when communication resumes after the GoodWe inverter’s nightly shutdown.

My Theory:

It seems that when the Modbus TCP connection re-establishes, there might be a “stale” or cumulative value sent in the first data packet that the GX device interprets as a massive instantaneous power spike. However, because this happens so quickly, it doesn’t seem to make it into the long-term logged data (Advanced tab), yet it remains visible on the Overview dashboard.

Has anyone encountered similar behavior with GoodWe inverters or other Modbus-connected PV inverters? Is there a known way to “debounce” this initial data or a setting in the GX/Ekrano to ignore these startup spikes?

Any help or suggestions would be greatly appreciated!

exactly. If your inverter reports 7.5 kWh “out of a sudden” that is not recorded to go anywhere (grid, battery) - then it’s mathematically considered consumption.

Can you see if the EnergyForward Counter of your Goodwee does reflect that spike as well? (The bar graph is calculated out of the counters, not out of the momentary values)