I have a system that consists of one 15kW Quattro, three Smart solar MPPTs 250/100, one Cerbo plus 15 X US5000 Pylons.
Before we added the last five US5000, the SOC showed as a percentage on the VRM. After adding the extra five batteries, the SOC has disappeared.
I have changed the cable connecting the battery to the Cerbo, made sure it is the correct way around. Changed the Cerbo for a new one, makes no difference.
The VRM recognises the Pylons on the VRM under battery but does not show the battery under devices. The Cerbo show under the Gateway but not on the device list. I am not sure it ever did.
I set the battery monitor to automatic hoping it would pick up the Pylons but it chooses the Quattro as only option showing.
This system runs totally off grid so the SOC is important worked before so I am baffled as to why it does not work now.
In addition to @Chris78 commenets can you provide a photo of the daisy chain stacks, I added two new ones to my stack and wondered why I wasn’t seeing SOC because the A/CAN wasn’t connected ie it was in the B/RS485 port it was dark and late I’m stinking to that excuse
I have tried making one of the new batteries to Master, also one Pylon engineer told me to set all dip switches to zero, contrary to the manual.
@Daza A/Can is connected one the first in the stack, and outgoing plugged into the LinkPort 1 and daisy chained to Linkport 0 to the next battery and so on. The last battery is connected via Linkport 0 and has a terminator in Linkport 1.
I can remove the terminator, but it did not work before I put in in.
@Daza My problem is that that the battery is not showing up in Devices at all. Although under Batteries, the system acknowledges the Pylontech battery.
Have you got terminator in the GX next to the VE.CAN? And yes as please photo like @M_Lange suggested. as fault finding I would start with a stack of 4 or 5 depends how they are stacked and only turn on a stack see if it registers then off and connected them one at a time till you find the issue or the culprit