SmartSolar MPPT 150/35 12v Settings Suggestions appreciated.
I have the MP2K, DC/DC, M10, and MPPT 150/35 12v, Smart BMV 712 Shunt.
One VATRER 300Ah battery.
Only 2 roof panels on Airstream 16X that are only 80w each.
Problem Symptoms, or is it as it should be:
Panels deliver to the MPPT, MPPT output fed to M10/Lynx.
All night the MPPT is pinging the system and drains the battery substantially.
Logic to me is that after sunset the MPPT should drop to a “sleep” mode.
Second question: Battery is at 13.8V as VATRER factory spec requests, YET when I have the breaker feeding from MPPT to the M10, the fully charged system is driven into Bulk and these two little panels will not begin to bring the battery up to 14.60 volts.
Pondering, until I invest in much larger wattage roof panels too replace the 80’s, I just leave the MPPT disconnected from the entire system.
Make sense, or are my setting wrong, etc. Suggestions appreciated. Jack
The tech specs for that battery say that 14.6 is the maximum charge voltage; I would never advise charging an LFP battery at the maximum voltage, since that drastically increases the chance of the BMS shutting down. Better to go for 14.4v charge voltage.
Not really; standby current of the MPPT while not charging is ~20mA, so that’s as close to “sleep” mode as you’d be likely to see from anything.
Here is what is in the VATRER Users Manual, battery received in the last month and working perfectly.
I too was surprised, but pondering at the 14.4V might be wiser?
I think you are right, will alter that today.
Now, back to the MPPT issues.
So ignore the MPPT always dropping into a full recharge pattern when the battery is at 13.8 Float per MP2K?
Not sure what you mean here; if the MultiPlus is in Float, that means you’re plugged in, but still no harm in the solar charger adding a bit of top-off if that’s the question.