I recently installed a (home) battery system myself.
The system consists of the following components:
MPPT 450/100
Lynx Distributer
Multiplus 48V / 4K5 (connected to 1 phase with backup power)
3x Pylontech Fidus (BMS-connected)
Victron VM-3P75CT
Cerbo GX
I now have the system up and running and have been using it for about a week with ESS/DESS. When setting up the ESS assistant, I was asked for certain values that aren’t specified in the Fidus manual. So I asked Pylontech for advice, and they suggested I ask Victron (I called my supplier, but they hadn’t dealt with this battery before either, as it apparently is still quite new). There’s a lot of information online too, but not the exact values. The system is currently running with the following settings (without any issues so far), but I’m curious to hear what you think:
Sustain voltage 48.00V
Cut off 0.005 C = 50.00V
Cut off 0.25 C = 49.00V
Cut off 0.7 C = 48.00V
Cut off 2 C = 47.00V
Restart off-set 1.2 V
A few other general values:
Absorption voltage 56.8 V
Float 54.00 V
DC input low shut-down 37.20 V
DC input low restart 43.60 V
DC input low pre-alarm 43.60 V
I also came across various values online for DESS regarding the import and export power limits. Mine are currently:
-Import 17 kW (based on a 3x25A main connection)
-Export 7.3 kW (combined output of my MPPT and Growatt AC inverter).
I’m curious to hear what you think and whether anyone else has this setup. In any case, I hope this helps make more information available.
Use the 15s values on the established page and ÷by 15 and multiply by 16.
Example
Absorption 52v for 15s value
52÷15 = 3.467
3.467 x 16 = 55.46/7 or 55.5v like many other 16s batteries
They will be more sensible than the ones you have set there with safety margins.
I detest those battery voltage range datsheets the battery BMS almost never allows that range - ever.
Leave the BMS to do it’s thing unless you face some issues.
Take note of the vrm advanced and see what it is reporting there for CVL etc. and how happy the battery is.
These in particular are too low. They are even too low for the 15s range.
Summary
Inverter Settings
In the Inverter tab of VEConfigure
VEConfigure Inverter Parameter Setting
DC input low shut-down 44V
DC input low restart 48V
DC input low pre-alarm* 48V
The pre-alarm setting is dependant on your preference and on site specific requirements. You may wish for this to be activated earlier in an off grid situation to allow time to start a backup generator.
Thanks for your reply and for thinking it through with me!
I’d deliberately kept the settings somewhat conservative, as I was still waiting for the official parameter values from Pylontech.
Your suggestion to convert the values for 16 cells sounds sensible. I’ll try these settings and monitor via VRM Advanced how the battery and BMS respond.
I’ve connected Victron to Home Assistant so I can also keep track of the different readings while charging and discharging, and how they relate to the battery’s charge level. Hopefully that’ll give me a better idea of what’s good for the battery. I’ve set 20% as the battery’s lower limit, and it would only discharge further in the event of a power cut.
Ideally you want the system to shut down before the BMS hots low protection not the other way around.
@Erwin1989
My apologies about the previous post.
It is bad advice with the voltages.
I see the Fidus is 48v not 51.2. I think mixed it up with something else.
Looking at the datasheet there is no reason why using the pylotech Victron page recommendations won’t work. They have the same voltage range as the us 3000s 52.5 to 53
You were right about the 51.2V; this datasheet is for an “older” model. The new models (which I also have), Pylontech Fidus FB-L-5.12-EU, are indeed 51.2V.