SmartSolar MPPT 100/50 not following absorption settings

I have the SmartSolar MPPT 100/50 set to Absorption duration Adaptive, Maximum absorption time 6 hours, tail current 2A (the defaults). It went to float after just under 1 hour when current was 18.4A. I have another identical setup that works properly. Both are on the same software version, both have the same solar panels, battery and monitoring, both are brand new.

Am I missing something here? I’m trying fixed mode today but shouldn’t it have stayed in absorption until either the current hit 2A or the time hit 6 hours?

It won’t stay on until the maximum that is just a backstop.

Adaptive charging stays for as long as it feels like.

No two setups will be the same.

I switch it off as I believe it is a sure fire way of undercharging LA batteries and thus in the long term causing damage.

I know the maximum is the maximum, but shouldn’t it stay on until EITHER the maximum or the tail current is reached? It didn’t get to either one.

In theory I suppose it should.

From observations over the last 25+ years with chargers set to adaptive it always goes into float way to early. Hence why I stopped using it.

Try swapping the units over, if the reaction moves with the charger then it could have a faulty algorithm, if it stays put then obviously it hasn’t.

Easy to say, hard to do - it’s 13 miles away from me. Maybe I will when I get out there next time.

From Victron on adaptive charging:

The absorption time of a Charger will adapt itself as follows:
after each period of bulk charge (= the charger has reached its maximum current) an absorption period of 20 times the the bulk charge period will follow, with a maximum set at, for example, 4 hours.

So if one battery was fairly full then it would take a short bulk charge and the Absorption charge would be short. If the other was at a lower SOC then it would be correspondingly longer charge.

Were the two batteries at the same SOC when they started?

The bulk charge period that day was 2 hours 40 minutes. The absorption period was 55 minutes and ended at 18.4A.

The two systems were not at the same state of charge, but only different by a tiny amount (about 3%). The one that stopped absorption early was the one at the lower state of charge.

I thought the end of bulk charge was at the absorption voltage set point, not the maximum current set point (I’ll never get to maximum current).

If you want to reliably use tail current to end absorption I found using fixed absorption the best option to force it to continue until the tail current was satisfied. Just make sure the tail current is suitable for your battery type and capacity.

Thanks. I’ve set that up but it’s cloudy today so I probably won’t be able to tell if it worked until our next sunny day, which is Wednesday.

Well, the sun came out this afternoon, unexpectedly, and that seemed to work. It dropped out of absorption into float at the same moment the current dropped below 2A. Thanks!