Shore current limit input bug in v3.52

I’m trying to set the “Shore current limit” on paralleled MultiPlus II 48/3000s. New UI will only allow to change AC Input 2, which doesn’t exist on the MP-IIs. Switching to the classic UI still allows changing the correct setting. It’s the same issue through the quick side menu and through the device details page.

System: Cerbo GX, Touch 70, 2x MP-II 48/3000 Parallel, LFP Battery w OrionJr2 BMS

Did you disable the input 2 in system set up?

Yes, AC Input 2 is set to “Not available”. See screenshot.