Cerbo Input Current Limit disappear. Bug?

Hi everyone,

During my ongoing struggle with the setup GRID → inverter PV → ESS → AC IN → 3 Multis in parallel (you can follow the thread here:

) I encountered this issue.

When I restart the Multis and reconnect to the Grid, the Input Current Limit setting in the Multiplus settings disappears:

image

However, if I reboot the Cerbo, the Input Current Limit setting comes back and is visible again:

image

Is this a bug or a “feature” ? :slight_smile:

Let’s start with what firmware you are running? On the gx and on the inverters.

Thanks Alexandra

Multis are in v.552
Cerbo is v3.42
VM-3P75CT is v1.06

Hope this helps !

That’s because the /Ac/NumberOfAcInputs path on dbus is having a value of 0 during MP2 reboot.
And this [ NumberOfACInputs different than 0 ] is a condition for the Input Current Limit to show.
The same with the State of charge below.
And more, but I suppose you didn’t see them… :slight_smile:

It needs a dbus read refresh, but maybe in the future releases… :wink:

1 Like

Yes you are right, also the SOC! I didn’t notice that !

1 Like