I have an installation with a SmartSolar 150/85 VE CAN connected CERBO through VE Direct cable .
The Smart Sollar erratically switches off during the day and chrge current drops to 0 A , with PV Voltage > 80 V and connected to the battey (52 to 54 ) , Remote contact is closed. Opening an closing the remote contact does help .
After the charging has ceased the only way to get it back to work is
by deactivating via VictronConnect ( Bluetooth or through Cerbo ) or by setting mode Register to 4 ( off ) via Modbus
wait at least 5 min
and then reactivate resp. set mode Register to 1 (= on ) via Modbus
firmware version whas been updated to 3.16 which did not help at all .
I would appreciatye any help
Kind regards to everybody
Yes, this was actually my first test I disconnected the CERBO and - few hours after sunrise it ceased charging the battery ( < 60% charged ) it deactivated itself. The only way to restart was by connecting Victron connect on my smartphone via bluetooth , deactivate the charger and re-activate few minutes later.
There is no alarm , PV Voltage > 80V , Bulk mode , battery voltage approx 53 V - way below absorption of float voltage
Hi Mike
Three days ago I eliminated the VE Diirect cabling and connected the Smartsolar and CERBO via CAN Bus - and since then no more erratic deactivation - I will wait now