slowly making my dream setup. The goal is to power my house and my garage based hobby workshop in off-grid mode for most of the year.
Key information:
- my house has 3-phase grid connection (3-N-PE)
- house AC loads are distributed between 3 phases but not balanced (not possible to balance, i.e. kitchen 1-phase circuit powers 2kW kettle, 0.8kW toaster, 0.8kW microwave oven, dishwasher (maybe 1kW heater?). Induction cooker is 3-phase but unbalanced.
- hobby workshop machines are mostly 3-phase induction motors 400 VAC - the biggest load is air compressor 5.5kW, milling machine 3.7kW, lathe 4.0kW, welding machines (both 1-phase and 3-phased powered). Of course i’m not going to use all of them at the same time but the worst case scenario would be using CNC plasma cutter - this will require air compressor (3ph-5.5kW starting occasionally) + plasma cutter unit (Hypertherm XP45 on 3 phase 400 VAC power on full load consume almost 7kW) + XY table (servo motors + PC, assuming 2kW peaks, couple 500-700 W normal). So this can theoretically draw ca 13kW @ 3ph-400VAC! This will be very rare situation however. What if my wife makes a coffee (2kW kettle) while washing clothes in washing machine?

- i’m going to install 3 air condition units (total max consumption 3-4kW)
- i can’t feed energy into the grid - zero feed-in. In fact most of the year i plan to be disconnected from the grid.
Already installed or purchased:
- Three Victron Multiplus II 48/5000-70-100 units
- 6 x 420Wp PV panels (facing West) connected to Victron MPPT 150/35 charger
- 10 x 500Wp PV panels (facing East0 connected to Victron MPPT 250/85 charger
- experimental DIY battery (ca 5-7kWh usable energy, old Chevy Volt Li-Ion 12S modules)
- Victron Smart Shunt 500A/50mV installed on the battery
- Cerbo GX + 7” Touchscreen
- 32 x 324Ah LiFePO4 cells waiting for DIY enclosure
- 4 x JKBMS 300A V19 and other bits to make four 16 cells banks
Plan to buy/install:
- 32 x 324Ah LiFePO4 cells for total 64 pieces system (ca 66 kWh of energy total, in 4 banks)
- install additional 500Wp PV panels - 12 or 15 pieces on East side and 12 or 15 pieces on West side roof (35 deg inclination)
And here comes the story - to add those additional PV panels i can see two scenarions:
A) DC coupling by adding MPPT SmartSolar charger/chargers
B) AC coupling on AC-OUT side of the MP II’s using Fronius Symo 12.5-3-M
From what i’ve read here and there, for option A pros are:
+ more efficient charging of the battery bank (DC-DC)
+ not loading MP II because MPPT chargers load energy to battery directly
+ system doesn’t care about unbalanced loads on AC
Cons are:
- AC loads are powered by MP II’s only (grid disconnected/off-grid scenario) so MP II 48/5000 can deliver “only” 4000 W / 5000 VA per phase (i’m starting to regret i didn’t buy MP II 48/8000 units…)
For scenario B pros:
+ much more load available in sunny days as i can theoretically get 15kVA from MP II’s + 12.5kVA from Fronius
+ driving AC load using solar power directly from Fronius is more efficient
+ i can but second hand Fronius quite cheaply
And now how about B scenario cons?
- grid connection preferred to be able to dump excess energy spikes (when battery is full, sunny day and big AC load suddenly stopped)
- frequency shifting (Victron-Fronius “communication”) is slow to handle situation described above
The biggest concern is AC load balance - lack of balance to be precise. I heard that AC coupled Fronius is not an option in off-grid scenario because the way Fronius works - it needs balanced 3 phase load. Is it truth? My case will never have all phases balanced.
Some notes:
- no, i’m not using air compressor and plasma cutter every day. In fact this is rare situation
- priority would be to have reliable power for house loads. 99% of the time in the year my garage workshop is not in use
Final thoughts i have now:
- is it better to consider connecting grid on MP II’s AC-IN’s to allow Multiplus to pass the energy from the grid in case i use big load? I’m afraid Victron will feed-in some energy into the grid occasionally due to the way it is designed (even if zero feed in is set) - is it truth?
- to balance 3 phase loads i can use air condition units (one unit per phase) + some Nore-RED logic to switch them individually on/off as required to help balance the load
I’m really confused regarding limitations of using AC-OUT side AC coupled Fronius in Victron micro grid system.
Thank you for pointing out weak points in my assumptions, guys!