Hi all. Quattro 12/3000/120, small microprocessor running firmware 1931125, nothing connected to the ve.bus ports, no remote switch, jumper is in place.
Quattro was working fine, I diagnosed a failing output circuit breaker in the Victron iso trans supplying it which was opening under heavy load. The breaker arced on reset during troubleshooting.
After the breaker arced, the Quattro now doesn’t boot - as soon as it’s switched to On or Charger Only, all 8 LEDs come on solid, which isn’t a recognised fault code. Sometimes, all except Inverter On LEDs come on but 9 out of 10 power cycles, all 8 are on. This only happens on DC, on AC only it’s completely dead.
It doesn’t connect to VEconfig at all. VEflash recognises the Quattro is turned on, prompts for a reset (power the Quattro off then on again) but after that it comes up with the dreaded ‘could not connect, please try again’ message.
Other steps I’ve tried:
- Disconnecting AC and DC inputs, waiting 5 minutes, reconnecting DC.
- Reseating all ribbon connectors
- Disconnecting external temperature sensor
- Checking DC input - this is within range at 12.7v.
- Disconnecting all AC cables
Guessing the transient from the arc has fried something inside, I’ve never seen this before! Any other suggestions? Thanks.