Hello everyone,
I would appreciate your advice regarding an incident with one of my Quattro 48/10000 units.
My main working system is currently based on a Multi RS 48/6000. Later I upgraded the installation and added three Quattro 48/10000 units, intended to be configured as a three-phase VE.Bus system.
The three Quattros are connected together through VE.Bus in a daisy-chain arrangement and connected to the Cerbo GX through a separate MK3-USB interface, not through the built-in VE.Bus port of the Cerbo GX.
All inverters are connected to the DC bus through a Lynx / power distribution system with fuses. After the DC input section I have a custom pre-charge module with a switch and a pre-charge push button. Before turning on the main rotary DC switch, I hold the pre-charge button for about 30 seconds.
This is my second high-power Victron installation. Previously I installed several single-phase Victron systems and also one three-phase system based on MultiPlus-II 5000 units, which I still maintain and regularly update. On that three-phase MultiPlus-II system I usually update the firmware of all inverters together, not one inverter at a time as I did in this case.
About one year ago I made the main DC, AC wiring and VE.Bus connections for these Quattros. I do not clearly remember whether I had already configured them as a three-phase system at that time. However, since the inverters were able to start individually one by one, most likely I had not yet configured them as a three-phase system.
Each inverter had previously been tested individually in single-phase mode and worked correctly.
The AC wiring was prepared, but no AC input source and no AC output load were connected during this incident. The AC input neutrals are connected together separately, the AC output neutrals are connected together separately, and the PE / grounding conductors are also connected separately.
Then the project was paused for about one year. During this time all three Quattro units, including the second Quattro that failed today, were switched off using their front rocker switches. However, they remained connected to the DC bus and therefore were still under DC voltage. The site itself was powered through the Multi RS 48/6000.
Today I decided to update the firmware and configure the three Quattros as a three-phase system.
The sequence was as follows:
-
I first switched on each Quattro individually using its front switch, checked that it started, and then switched it off again after about 30 seconds.
-
Then I started again from the first Quattro, switched it on, updated the firmware successfully, waited until the process was complete, and switched it off.
-
I then switched on the second Quattro. It initially powered up.
-
After that I triggered a device rescan from the VRM / device list. At that moment there was a loud pop and smoke came from the second Quattro. The Cerbo GX also started beeping.
-
I immediately switched everything off using the inverter switches and turned the main DC switch to OFF.
-
After some time I restarted the DC system: first by holding the pre-charge button for about 30 seconds, then by turning the main DC switch ON.
In the logs there was something that looked like a short-circuit event on the Multi RS, but I do not believe there was an actual short circuit on the Multi RS. The Multi RS continues to work normally, and the load was transferred back to it through the ATS.
I tried to start the second Quattro once more. It attempted to start, but again made an abnormal sound and produced smoke, so I immediately switched it off again. I have not tried to start it since.
After that I tested the third Quattro. This time I did not immediately trigger a VRM rescan. I waited a little, then started the firmware update. The update process seemed to start and finish, but the firmware version did not actually change. I tried again with the same result.
Then I powered everything down and started again, this time switching on only the third Quattro. After waiting for some time and then doing the rescan, the firmware update completed successfully.
Important details:
-
No AC input source was connected.
-
No AC output load was connected.
-
The AC wiring was prepared: input neutrals are connected separately, output neutrals are connected separately, and PE / grounding conductors are connected separately.
-
Only the DC side and VE.Bus communication were active.
-
All three Quattro units, including the second unit that failed, had been switched off by their front switches for about one year, but remained connected to the DC bus.
-
The installation has DC fuses and a pre-charge circuit.
-
The Quattros are connected to the Cerbo GX through an MK3-USB dongle, not through the built-in VE.Bus port.
-
This connection method was chosen because the Multi RS is the main working system on this site, while the VE.Bus Quattro system is intended to be a secondary system visible on the VRM portal.
-
Photos of the installation and the damaged unit are attached.
-
I have already contacted my dealer and sent photos of the installation.
My questions are:
-
Could the firmware update or VRM device rescan realistically trigger such a hardware failure, or is it more likely just a coincidence?
-
Could the fact that all three Quattro units, including the failed second unit, were connected to the DC bus for about one year while switched off by their front switches have contributed to this failure?
-
Before commissioning or firmware updating a VE.Bus system that has been sitting connected to DC for a long time, is it recommended to fully disconnect the DC supply, wait several minutes for capacitors and the GX system to discharge, and then restart everything from zero?
-
Is it acceptable to start a firmware update when the VE.Bus system is connected to the Cerbo GX through an MK3-USB dongle, rather than directly to the built-in VE.Bus port of the Cerbo GX?
This connection method was used because the Multi RS is the main system on the site, while the VE.Bus Quattro system is intended to be a secondary system on the VRM portal.
I understand that the damaged inverter should be inspected by the dealer/service center, and I do not plan to open it myself. I am mainly trying to understand whether I may have made a commissioning mistake, or whether this looks more like an internal hardware fault that happened to appear during the update/rescan process.
Thank you for any advice.